Thought I'd test the Aquastat and damper control. Now that I got results in front of me i don't know what I got.
Test 1 Water temp gauge reading 180 Aquastat set at 175 Damper closed.
I slowly turn dial on Aquastat till it clicks at 210 degrees damper opens.....turning the dial down from the 210 click the damper closes at 190 degrees Both seem to work which was my intent for the test.
Test 2 Water gauge temp is 172 degrees Aquastat set at 170 Turning the dial up again the damper opened fully at the 196 degree mark letting it burn at the new setting of 196 (approx) The damper stayed open till the water gauge read 190 then slammed shut. I took my Infra red tester and check the water and the water was reading 199 degrees.
Couple interesting side bar results is the water at the top of the boiler was 172 and the water at the supply fitting at the bottom of the boiler was reading 125 degrees the second test the top was reading 199 degrees and the supply fitting reading 165 degrees
What do you guys make of these results???
Thanks
Test 1 Water temp gauge reading 180 Aquastat set at 175 Damper closed.
I slowly turn dial on Aquastat till it clicks at 210 degrees damper opens.....turning the dial down from the 210 click the damper closes at 190 degrees Both seem to work which was my intent for the test.
Test 2 Water gauge temp is 172 degrees Aquastat set at 170 Turning the dial up again the damper opened fully at the 196 degree mark letting it burn at the new setting of 196 (approx) The damper stayed open till the water gauge read 190 then slammed shut. I took my Infra red tester and check the water and the water was reading 199 degrees.
Couple interesting side bar results is the water at the top of the boiler was 172 and the water at the supply fitting at the bottom of the boiler was reading 125 degrees the second test the top was reading 199 degrees and the supply fitting reading 165 degrees
What do you guys make of these results???