More questions on pex install

Arborist Forum

Help Support Arborist Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

sw18x

ArboristSite Operative
Joined
Sep 22, 2011
Messages
173
Reaction score
41
Location
NY
I have a 2550 square foot farmhouse. The house came with an OWB that is rated at 225,000 BTU/hour maximum output. 180 degree water pumps from the woodburner through ¾ inch pex tubing into the basement over a 65 foot run. Once the water enters the basement, it flows through another 30 foot run of ¾” pex tubing before entering a SuperStor Ultra indirect fired hot water heater. Water from the woodburner runs through the heat exchanger in the Superstor, thereby heating the water in the Superstor which then heats the house via baseboard heat. As a side note, the water from the Superstor actually flows through a gas fired boiler first before heading upstairs, with the boiler acting as a backup for the house if the wood furnace can’t keep up with demand. However, for our purposes let’s ignore the gas boiler because my goal is for the wood furnace to meet the full demand of the house.


There are a few problems with this set-up, which I inherited from the previous homeowner. First of all, the underground pex tubes are leaching a ridiculous amount of heat into the ground, to the tune of 15 degrees over the course of the run into the house. As a result, I am in the middle of installing insulated pex lines, either Thermopex or Logstor Pex-Flex, on the underground run to the house. However, after spending two days digging, replacing one broken septic pipe, one underground gutter pipe, and tunneling under a sidewalk, I want to make sure I do this absolutely right the first time. Here’s my dilemma:

Thermopex uses ¾” ID pex tubing. Pex-Flex uses a true 1” ID. By all accounts, Pex-Flex is a slightly better product, even though documented Thermopex failures are extremely rare. A buddy of mine is a heating/cooling professional and will be helping me make my final connections in the basement, but he won’t be free until September. Meanwhile, I have an open trench and a wife who wants her gardens back, so I need to make a decision between the two products this week and get the pex buried in the ground. The big question is, is it worth the extra 3 dollars a foot for Pex-Flex, and the extra hour drive to the dealer, to increase the size of my pex from ¾” to 1”? I’m tempted to go with the larger Pex-Flex so I can get more BTUs into the house quicker, but if I do so, then I will need to replace the two 30 foot runs in the basement with either copper pipe or a true 1” non-insulated pex, and I don’t know pricing on these materials. I also don’t know how much more BTU’s the larger ID will give me. Predictably, the Thermopex dealer says the 1/4" difference in ID isn't a big deal and the Pex-Flex dealer uses the larger ID as a selling point. To throw another wild card in the mix, I’m fairly certain the SuperStor setup isn’t ideal: currently, the heat exchanger in the SuperStor can’t keep up with demand, so we may end up going with another type of heat exchanger once my buddy takes a look at everything and tweaks the system. (He mentioned a steel plate heat exchanger and the outdoor wood burner manufacturer included info on “Flatplate” company products in the owner’s manual). Then again, once I’m running 180 degree water into the house with the insulated pex instead of 165, maybe the SuperStor setup will be sufficient.

I’d appreciate any advice on this. I just don’t have the knowledge to run the formulas to see what I really need in terms of volume/flow/btu’s. A few more pieces of information that might help:

· Although we blew in insulation, the house is not very efficient in terms of heat loss (old drafty farm house).
· Right now I’m using Taco pump model 007-F5, 1/25th HP .71 amp 3250 RPM (I don’t know what the gpm’s are with this pump)
· The woodburner also heats a radiant floor setup in my 4 car garage, so I’m close to the maximum square footage this furnace is rated for (3800 square foot total house and garage, I think my model is rated for 4k or 4500)
· As of right now I’m leaning heavily towards buying the Pex-Flex and having the dealer install fittings for 1” copper onto it (Pex-Flex takes special fittings), I figure that way in the short term we can just use an additional fitting to temporarily step back down to ¾” for the basement run or later on go with 1”. That is, unless I have 20 guys on here telling me I’m crazy because there’s no way I’ll ever need the extra ¼” and ¾” will be sufficient in all applications.

Thanks for any input!
 
I don't have any experience with either of those brands, but generally speaking - bigger is better & I'd go with the 1". There might also be some potential savings from reduced pumping requirements with bigger pipe - the 1" will flow a lot more BTUs that the 3/4 all else being equal (0.79 sq.in vs. 0.44 sq.in. cross sectional area). Sounds like it's only a couple hundred $$ different, and as you say you want to try to get this right while the yard is tore up.

The only thing that would make me consider the 3/4 over the 1" is if the 1" is an inferior product, heat loss & durability wise.

Flat plates are very good at exhanging heat, I'd say a lot better than the Super Store. But the Super Store would also give you a bit of a buffer - although not really that much. Super Stores also aren't really designed for that - I'm not sure if the higher heating temps would affect its life or not? Usually in heating DHW, they shut the heat supply down when the tank temps get up around say 140 or so - which is about the lower limit of usable heating water temps. I think you would definitely see an improvement in how much heat makes it to your rooms by using a flat plate, as long as its sized right (big enough). There are lots of variables involved in proper sizing - flow rates on both sides & temps in/out & all that. Something I haven't gone through myself.

My seat of the pants is telling me that by fixing your underground pipe, and using a flat plate, you would be heating your house with almost the same amount of heat you were losing to the ground before. Generally, a delta T of around 20° (difference between supply & return) is considered a good number to aim for.
 
Hi,
Given equal head a 1" pipe will flow almost double the GPM of a 3/4" I am kinda an over kill type as opposed to squeaking by if you know what I mean? My system just idles to do it's work of heating the home, shop and water and I like it that way but I know about cost concerns because I had them too. I spent lots more than minimum to install mine but all is forgotten now after 6 years of no problems and all the heat we need.

Id go with 1"

Just in case you hadnt figgured that out? LOL :msp_tongue:
 
ThermoPEX is also available in 1-1/4 inch size. I plead ignorance regarding the other brand.

My run from the CB 5036 OWB is around 65 feet; I used 1-inch ThermoPEX but have forced-air heat. We heat our domestic hot water, the house (1700 ft^2 and the attached garage (700+ ft^2) with the OWB.

Jon
 
Thanks guys. As I continue to research it becomes clear that bigger is better. I have the same concerns about the Superstor. The past two seasons water temp in the Superstor maxed at 150 degrees (that's as hot as I could get it, and only in between cycles would it reach this high). With more gpm, more btus, and less heat loss to the ground, I'm wondering how high can I heat the Superstor? 180 degrees? Seems to me I remember trying to contact the manufacturer in the past with no luck to get an answer to that question. I do know the warranty states that heating water above 150 qualifies as commercial status as opposed to residential and compromises the warranty.

Your statement about heating the house with the amount of heat I was losing to the ground is exactly why I shut down the house early last year and stopped loading the furnace with my primo seasoned locust - after all the hard work getting my wood I couldn't stand feeding it to the ground!
 
Thanks guys. As I continue to research it becomes clear that bigger is better. I have the same concerns about the Superstor. The past two seasons water temp in the Superstor maxed at 150 degrees (that's as hot as I could get it, and only in between cycles would it reach this high). With more gpm, more btus, and less heat loss to the ground, I'm wondering how high can I heat the Superstor? 180 degrees? Seems to me I remember trying to contact the manufacturer in the past with no luck to get an answer to that question. I do know the warranty states that heating water above 150 qualifies as commercial status as opposed to residential and compromises the warranty.

Your statement about heating the house with the amount of heat I was losing to the ground is exactly why I shut down the house early last year and stopped loading the furnace with my primo seasoned locust - after all the hard work getting my wood I couldn't stand feeding it to the ground!

Sorry I wasn't around to help with the selection but I am still curious what you did?
Your setup with 1" ThermoPex or equiv. should not need a big pump.....

Curious to know what you did
 