I have a 4436 CB. The controller is from CB and made by dwyer. I ordered a spare from love controls division, dwyer instruments. The sheet that came with the new unit has instructions to unlock, lock and make changes. I used these instructions on the unit on the 4436 and it works the same.
Access to all code protected parameters
Press set for 8 seconds. The access code value 0 is shown on the display (comes from factory with 0)
With up or down arrows, code can be set to user needs.
Press set to enter the code. if code correct, the first parameter label is shown on display (sp)
Move the desired parameter with up and down keys.
Press set to view the value of the display.
The value can be modified with the up and down arrows.
Press set to enter the value and exit.
Repeat until all necessary parameters are modified.
Press set and downat the same time to quit programming or wait one minute and the display will exit programming mode.
*the keyboard code and be reset to zero by turning off the controller and turning it on again while keeping the set pressed.
PARAMETER DESCRIPTIONS
SP = Set Point. Temperature wished to regulate the machine. Can vary
from r1 to r2.
r0 = Differential. Heating: If temperature is ≥ Set then out OFF. If temperature is ≤ Set then out OFF. Cooling: if temperature is > Set + r0 then
out ON. If temperature is ≤ Set then out OFF.
r1 = Lower Set Point Limit
r2 = Higher Set Point Limit
d0 = Heat or Cooling Control. Ht = heating control, Co = cooling control.
d2 = Defrosting Time Remaining, in minutes. If d2 = 0, defrosting will
not start.
d8 = Interval Between Two Defrostings, in hours.
c0 = Minimum time for compressor to be OFF. Minimum time from
when the compressor stops till it connects again.
c1 = Continuous Cycle Time. The remaining time for a continuous cold
cycle.
c2 = ON time of fault cycle, during probe error.
c3 = OFF time of fault cycle, during probe error.
P1 = Ambient Probe Calibration. Offsets degrees to adjust the ambient
probe.
P4 = Decimal Point. Display decimal point in normal operation. Always
present in parameter menus.
H5 = Access Code to Parameters. Factory-set as 00.
H6 = Ambient Probe Type. Sets probe type to be NTC or PTC.
t0 = Temperature Display Limit. Maximum temperature shown on the
display, although the real temperature can be greater
Hope this will help. If anyone has a problem finding the correct parameter I'll go unlock mine and post it here which one it is. Been a while and can't remember off the top of my head. But I think it's r0