ericjeeper
Addicted to ArboristSite
yep you need a faster pump.Currently ot is moving through the HX to slow and is dumping to much heat.
A 009 Taco should work from the owb to the HX. How well is your house insultated? When you say the unit can't keep up with the heat demand, when it is bitter cold, seems it could be lack of insulation in the house.
House is insulated but drafty and out inthe middle of nowhere and at the full mrecy to the weather and wind.
Your exchanger could be larger, set it on 2" foam board and wrap it in fiberglass insulation.
Are the 2 pipes running from the heat exchanger to the oil furnace hot the full length? Run your hand over the full length of both pipes, if they are hot where you can't touch them and then drop to warm then you have an air lock. I mean they should be really hot the full length of the pipe. An air lock can occur in the exchanger or near the pump. I had this problem this year, I had to bleed the air out of the boiler by cracking the Taco flange and adding water to my oil furnace, bled the air, then my house got warm....nice....
Pipes are very hot.... can't touch them.
I had air in both my exchanger and pump on my oil furnace side, I couldn't figure it out. The pipe from the exchanger has a 007 pump and was boiling hot, but when I ran my hand down to where the pipe enters the oil furnace it was only warm and I just couldn't get the oil furnace water up in temperature...I finally figured it out, I had air. Hope it's a simple fix....
Keep working on it...eventually you'll figure it out.
Yes, there is a wye at the HX and I just checked them a few days ago when all this started.
Something I might be forgetting to tell is that I have the water circulating through the oil burner with a 007 pump from the HX to the burner (right next to it). And as mentioned, the 009 feeds the HX from the OWB. Just amking sure that what is being said here is to replace the 009 pump at the OWB with a 7 or 11. Thanks everyone!
yep, that's where I got my 30 plate. I just want someone to tell me that I am doing the right thing and that I should go with the 50 as compared to the 40 or the 60.
ok, here is what I found out. When my upstairs and downstairs calls for heat, I get a drop across the heat exchanger of 45 degrees or more...so that is the temp of water going through my house and that is why I am not getting heat. I am only circulating 140-150 degrees of water and my house won't catch up.
Now how do I solve this?
The water temp coming of the OWB stays close to the set point of 195 and recovers pretty quick after a load. So doesn't that say the pump is doing an ok job or are you still suggesting that I get a 007 or 011?
I have bled these pipes about 50 times, there is not much more I can do for that.
Are you still losing 45° in the oil burner when both zones call for heat ?
you may have a restriction in the HX, OWB supply or return causing the low flow . even with the larger pump installed.
Yes, still a large drop. Install is new and flow is very good. I have tap -offs that I can run the water into a bucket and the flow is there.
Is the water temp of the OWB still recovering as quickly?
If you are getting the the full flow and pulling more BTU's from it , then it should take longer to recover.
Yes, OWB has no problem keeping up with demand.
Are you pulling the the hot water from the top or bottom of the OWB reservior ?
The water at the top of the OWB reservior should be the hottest as heat rises. Drawing the hottest water from the top will translate to more heat to the house.
From the top on both pumps.
And, What size lines are running from the OWB into the house ?
Most OWB owners will reccommend 3/4" or 1" lines. Larger lines are less restrictive and able to deliver more volume meaning more BTU' s to the house. A couple of OWB owners have reported satisfactory results with 5/8" line but I wouldn't suggest going smaller because of the restricion a long run would cause.
Maybe Im wrong,but I think your 30 plate is doing the job if its pulling 40 degrees off the water as it heads back to the OWB...I have a 50 plate exchanger,and Im so glad I went with it...with my incoming temps at 180,if i have one zone on,I lag 6-10 degrees lower at the oil fired boiler than the incoming temps,if a second zone kicks on it can drop 10-15 degrees below,a 3rd zone,and it can drop 20 degrees sometimes.I wouldnt want to see how much it would be dropping with a smaller HX.
Another issue could be if your pex lines are not separated by at least one wrap of insulation,the outgoing cold water that passed thru the hx cools off incoming hot supply side on its way back....this problem gets worse the more you pull out of the pex,as the temo differential gets larger,this becomes more of an issue...
Problem is, is that if one zone calls for heat, it drops 25-40 degrees off the HX. OWB side = 200, Oil Burner side = 165....two zones, 150, 3 zones...etc
Keeping in mind I have another pump going off the OWB to a radiator/fan to heat the garage...OWB STILL can keep up. The only variable I see is the HX.
OK, I am going to try a 007 since I have a new one on hand, if that makes a difference I am going to go ahead and get a 011.
Now, how is the 30 plate for my application. Still an issue or can't we tell yet?
My return lines are hot....