Do you have any type of priority controls set up? If not you may just be pulling to many BTU`s at one time for the boiler to keep up. When my infloor slab kicks on it`l suck my boiler temps right down. So I prioritized my zones with a controller.
what size is your pressure side HX pump for your boiler loop?Which way is the water flowing? I used the blow off and drains,put in Tee's on both and run a 3 speed grundfos on low,(60watts),and it works great.My entire loop including HX is only 16 ft,with the hx 3 ft over the top of the boiler.I used 3/4" copper for the entire loop.
i'll go ahead and throw in my two cents....
My dad's place has a natural gas boiler, and a few years ago we wanted to try to make it More efficient. we noticed that the when the gas kicked off, the flue kept right on drawing air. since the HX from the burner to the water is about the same as any other heat exchanger, the water that sat in the heat exchanger became room temperature really fast. since his boiler sat in an old unsealed basement, this was usually pretty cold. to fix it, we added an automatic damper to close the flue when the burners weren't on.
i wonder, where do you have the water to water HX in your boiler setup. is it possible that the burner HX in your boiler is bleeding off a lot of heat , letting it go up the flue? i suppose that would depend on the boiler setup and where it is in your house.
Just tryin' to stir the pot a little with some other ideas.....
I did notice that even when the water in the HX is at the 190 level, the water in the boiler is about 20 degrees lower. Do i need a bigger pump on that loop? I wouldn't think so but .....?
Yes . Otherwise your heat in the OWB just sits there outside instead of more of it being moved to the house. If you are still gettinmg that much of a drop in temperature you should increase the flow more still.
Even if the pump is pushing water out to the boiler that is less than 3 feet away?
Did you ever figure out if the OWB sits higher or lower than the pumps ? I'm in Kansas so flat ground is pretty much a given. If the OWB is below the house it might be having trouble drawing enough water uphill to the pump.
OWB is much higher than the oil burner.... a whole level up.
Are you heating the return line going INTO the oil burner or the water coming OUT OF it going to your baseboard heaters ? I'd be heating the water going to the baseboards not the water coming from them. And you might be already.
I am circulating the cold feed water going into the oil burner and out before the pressure valve.
When does the pump from the OWB run ? full time or only when there is a call for heat ?
Even if the pump is pushing water out to the boiler that is less than 3 feet away?
OWB is much higher than the oil burner.... a whole level up.
I am circulating the cold feed water going into the oil burner and out before the pressure valve.
(the OWB pump runs) Full time. There are no controllers on the circulators for the oil burner heat..they run once demand calls...whether it is up to temp or not. A controller would help I guess. Any suggestions on what to get? That is probably why I use so much oil if I run that.
Something keeps telling me you have a SERIOUS restriction in either the supply line or return line to the OWB. I don't remember you saying what kind of insulation or protection the PEX lines had in the trench. I'm betting that if you ran a flow check on the lines from the OWB one of them is plugged, kinked or smashed somewhere.
I have TSP for my connections. I can tell you that I am sure I do not have a restriction on the OWB lines. Before the season started I took out a wide bend and cut the lines to put in two 90's. Before the hook-up, I flushed the lines to make sure of that. Keeping in mind I have no temp loss from the OWB to the HX. I am almost positive that the poblem isn't in the OWB loop, but my plumbing loop.
Have you back flushed the HX to make sure nothing got past your WYE strainer before it was installed?
Not flushed since the above.
I'd even go so far as to check that the nipples on the OWB were drilled all the way out when they were welded to the it.
What keeps you from plumbing the OWB directly into the baseboard heat ? And using the controller from the Oil Burner to turn on the pump when there is a call for heat.
i just want to make sure i have this all straight...
when you describe where the HX is in your boiler loop, it sounds to me like it is meant to keep the water in the boiler hot all the time. is this right?
That is correct!
Let me ask like this, is there a direct path that the water MUST take through the HX, or is it set up so that the HX has its own loop to/from the boiler.
Has its own loop.
i would really love to see a picture of the HX and boiler so i can see how it is hooked up.
I will take one however it is going to be hard to show what is going on since space around the boiler area is tight.
It almost sounds to me like the HX is set up kinda like a side arm for DHW, but maybe that is just my wrong take.
Now that you said it that way, that is also correct. My theory was that the circulated water in the boiler would grab the heat from the HX and keep things up to temp. Especially if there was a time when there was no demand from the boiler, it would recover quickly.
It should be hooked up in line, basically spliced into the line, preferably after the boiler.
That is probably leading into my problem. I have the water from the fill going into the HX and back out through the blow off line.
sorry to ask for so much detail, but more info will help
Originally Posted by Bcat22
i just want to make sure i have this all straight...
when you describe where the HX is in your boiler loop, it sounds to me like it is meant to keep the water in the boiler hot all the time. is this right?
That is correct!
Let me ask like this, is there a direct path that the water MUST take through the HX, or is it set up so that the HX has its own loop to/from the boiler.
Has its own loop.
i would really love to see a picture of the HX and boiler so i can see how it is hooked up.
I will take one however it is going to be hard to show what is going on since space around the boiler area is tight.
It almost sounds to me like the HX is set up kinda like a side arm for DHW, but maybe that is just my wrong take.
Now that you said it that way, that is also correct. My theory was that the circulated water in the boiler would grab the heat from the HX and keep things up to temp. Especially if there was a time when there was no demand from the boiler, it would recover quickly.
It should be hooked up in line, basically spliced into the line, preferably after the boiler.
That is probably leading into my problem. I have the water from the fill going into the HX and back out through the blow off line.
sorry to ask for so much detail, but more info will help
I will get a picture of this and see if it shows what I did..
After flushing and back flushing the HX, plumb it directly into the path of the water GOING to the baseboards. To hell with trying to keep the water in the oil boiler hot. Just let the pump in the boiler push the water through the HX to the baseboards. This draws the heat needed from the HX on it's way to heat the house.
Pictures !
All of the above are good suggestions, but still no piping diagram/pics, it's kinda hard to diagnose without them.
Here's an idea of what may be happening IMO...
If your indoor heating system is traveling thru the oil boiler, your temperature loss/swing may be happening there...why?
The boiler, when heated by the water transferred thru the HX by the OWB, can cause an updraft thru the oil boiler, sending some (not all) of the heat right up thru the chimney. Check the line temp. of the supply/return pipes on the boiler where it comes into and out of the boiler...this has happened before.