I think what I want is a low temp limit switch with a manual override. The problem is I don't know where to look for it. I had hoped some of the shaver guys would chime in since I think they end up using the rancos.
The single stage Ranco will not perform this task. The dual stage Ranco might, but I haven't looked too closely at that option.
I'm installing this feature this weekend on my NCB along with a high-limit cut-out for the damper solenoid and blower.
I'm going to use a simple upper water heater thermostat (White Rodgers 756-1 or equiv.) set for around 110F with a standard light switch in parallel with it as a manual override.
My operating strategy is as follows:
Out of fuel, water temp drops below set-point, thermostat opens removing power from damper solenoid and blower. Unit sits there until I get back. Reload it and start fire again if needed. Flip override switch on to bypass cold thermostat. At some point after the boiler is up to temp, switch off override.
My pump will be controlled from indoors via a custom controller I've been working on. Currently, I've got it wired so that the main pump is wired in parallel with the furnace blower. I'm using the analog output of my Ranco and using it to control three separate functions:
1) Gas/OWB arbitration: If below a minimum temp (around 120 F), activate furnace in normal propane mode on house thermostat heat demand. If above set-point, turn on pump, delay 60-90 seconds (still working on this part), then turn on furnace blower.
2) Boil-over prevention: If boiler reaches high limit (190-200F), turn on pump to circulate water and "dump" excess heat by running it though the HX and tubing. My boiler tends to have the water temp creep upward as the door and ash drawer seals don't always get seated properly. Twenty minutes of circulation usually mixes the water enough to drop the boiler temp back to normal limits.
3) Vacation mode: If boiler temp hits a very low limit, perhaps 50F, run pump continuously to prevent freezing (vacation mode).
Since I datalog my system's operation, I can monitor both its current status and its recent history. My datalogging is running on an old laptop down in the basement running XP that is connected to my home network wirelessly. I can sit at either my desktop or at my laptop (anywhere in the house but usually next to my recliner) and see what is going on. As long as my internet connection is working, I can also log in from anywhere while away and see what the boiler is doing. :hmm3grin2orange: