You want to have a 20 degree differential at your emitter/exhangers no mater what the supply temp is. You also want to maintain proper velocity of water thru the pipes, too much causes problems and is not efficient. If you run less than a 20 deg differential you are loosing efficiency and wasting wood. same for excessive flow. So take temps on supply and return of each loop/zone. and adjust speed accordingly. infloor radiant is different , 10 deg is the norm and below 140 depending on type of floor. At the boiler the lower your operating temp the more efficient, longer burn times and more comfort. look up outdoor reset control. Just dont run the boiler below 140-150 or manufacturer min. This is condensing temp conditions. 180 at your house might be the same as 190 at someone elses. theres lots of variables. Pumps will flow more GPM and carry more BTU with hotter water, there are tons of charts on this for every kind of radiation device. ( fin tube, infloor type, cast iron rads,emitters, etc).
I dont know why some thing biggeror faster is better , in hydronics its always worse. 1 GPM flow@ 180deg carries 10,000btuh, so if you know your heat load or have a heat loss calc you can figure things out. If you find a big temp loss between house and boiler, when you have your proper 20deg diff at the exchangers, then you have bad underground lines. Proper loss for underground is >1 degree per 100' at 2ft per sec flow or 4gpm in 1" pex roughly. Running the pump at higher speed hides the temp loss but its still loosing heat to the ground. Logstor/Urecon has good charts on this info and recomended flow rates. Also check out Taco pump site for all the info and troubleshooting you'll ever need.
Mikie62
By the way, nice job on the 18 yr old Central. Love to hear a good story or stove running good. And the fact your on the same pump means it was done right.