Bronze pump horsepower

Arborist Forum

Help Support Arborist Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

urhstry

ArboristSite Operative
Joined
Apr 1, 2008
Messages
353
Reaction score
11
Location
Northeast PA
Hey guys, what horsepower pump are you using to circulate your DHW? Is 1/40HP enough? My run is only 75 feet. Thanks
 
Scott -

You shouldn't size a pump based on horsepower.

In order to do it properly, you will need to do some calculations:

Determine the BTU/hr you need to transfer to heat your house

Size the heat exchanger to meet this need

Determine the anticipated temperature drop across your heat exchanger

Calculate the flow rate of water needed

Calculate the friction loss in your piping based on the flow needed (Very important not to skip this step !!)

After you have done all of this then you can pull out the pump catalog of your choice and find a pump that meets your friction loss and flow requirements.

All this said and done, a Hardy H2 OWB ships with a Taco 009 which is 1/8 Hp. Other manufacturers seem to have there own "standard" size pumps that will meet most piping / heat exchanger setups.
 
Last edited:
Back