Wow - what a sucky day! Have some rep for pity's sake! :msp_thumbup:
So you went from 1/3 to 1/25 HP and see no loss in performance? If that's true, what it should be telling you is that you were over pumping your loop with the original pump, and that 1" PEX wasn't enough to keep the suction full, especially when the boiler overfired and the temperature approached boiling.
Increasing pressure increases boiling point, likewise decreasing pressure lowers boiling point. That is important because all of the outdoor boilers I am aware of are running open to atmosphere, which means that the boiling temperature of the water in them is 212F, as opposed to a pressurized system at 12psi, where the boiling temp is increased to 242F due to increased pressure. There are many pressurized systems running at 190 without cavitation, because the water isn't anywhere near boiling. When you run an open system near boiling, just the pressure drop caused by the pump's suction, coupled with the restriction caused by the suction piping, can drop the boiling point enough to make the water flash to steam at the pump inlet, causing cavitation and catastrophic failure. I don't know, but I suspect that's one reason so many outdoor boiler manufacturers mount their pumps directly to the boiler: it keeps the suction full and cuts way down on pump failure. That, and it's easy.
When you get ready to buy another pump, I'd recommend looking a little harder. There are HVAC supply houses in both Rockford and Dubuque as well as multiple sources on the net where you can purchase that same pump for about half what you gave for it from your "dealer."
Good luck.