Scott is right, 18 degrees is low for a temperature drop across the hot water coil.
You might want to check to see if the coil is undersized for your house heat load. The standard TACO pump on a Hardy H2 is good for a nomimal flow of ~ 5 gpm which combined with your 18 degree temperature drop only is allowing ~ 45,000 btu/h of heat transfer into the air.
You might want to check to see if the coil is undersized for your house heat load. The standard TACO pump on a Hardy H2 is good for a nomimal flow of ~ 5 gpm which combined with your 18 degree temperature drop only is allowing ~ 45,000 btu/h of heat transfer into the air.